The Distributed Control System reference design is a hardware and software platform for developing HART-enabled analog input and output modules (or nodes). DCS Modules are assembled from several existing reference designs:
The reference design provides software connectivity using the MODBUS protocol. Modbus is a ubiquitous, open, industrial communication protocol for which there are numerous open-source and commercial software libraries and utilities. It is a serial master-slave protocol where the master uses a set of standard commands to read and write registers on the slave device, and CRC error detection ensures data integrity. Reading a slave register can give information about the state and inputs of the slave and writing registers can change the state or outputs of the slave. The mapping of Modbus registers to application-specific functions is dependent on the end application, and the DCS reference design provides convenient access to all of the functionality of the analog input and output boards.
Several options for communicating with the hardware are provided or demonstrated:
The following is a list of items needed in order to replicate this demo.
Depending on the PLC/DCS Node configuration the power needs to be provided as follows:
Refer to the CN0414 and CN0418 user guides for detailed information on power requirements.
Block diagrams for PLC / single-node DCS and multi-node DCS systems are shown below. These systems differ slightly in their allowable configurations:
An ADALM-UARTJTAG board and a spare CN0416 can function as a convenient USB Virtual COM port to RS-485 adapter. Any RS485 adapter should work, if another is available. Isolated / Non-Isolated depends on the application and difference in ground potential between the host and nodes. Full-duplex operation is only supported in the PLC/single-node DCS configuration, as both TX and RX signals are driven continuously. Both single-node and multi-node configurations can use half-duplex.
| ADALM-UARTJTAG Setup |
The CP2103 device must be programmed as follows to control the DE signal on the CN0416. Configure Silicon Labs Xpress Configurator as follows to program the device:
| IO2 configuration | Mode: Push-Pull, Alternate Function: RS-485, Active High | |||
Once the CP2103 is programmed, unplug from the host computer and connect P1 on the ADALM-UARTJTAG to P11 on the CN0416 with a 2×5-socket, 100mil cable such as AMP A3AAH-1006G. Be sure to connect with proper polarity - pin 1 on the ADALM-UARTJTAG must correspond to pin 1 on the CN0416.
| CN0416 Setup | ||||
| Isolated Full Duplex | Isolated Half Duplex | Non-Isolated Full Duplex | Non-isolated Half Duplex | |
| S1 position | NA | NA | NA | NA |
| S2 position | 2 | 1 | 3 | 4 |
| S4 position | NA | NA | 2 | 1 |
| S5 position | 2 | 1 | NA | NA |
| S6 position | NA | NA | 2 | 2 |
| S7 position | 2 | 2 | NA | NA |
Configuration for each node is similar, noting that each node must be set to a different address (via S1 on the CN0416) and the most distant node must have its termination enabled (via S6 or S7 on CN0416.)
| CN0416 Setup |
(Full-duplex only valid in a single-node system.)
| S1 position | Any position but different from node to node | |||
| CN0414 Setup (if available) | ||||
| P1 position | Any position from MULTI configuration |
| P2 position | ||||
| P10 position | Any position to result a different EEPROM address from board to board |
| P11 position | ||||
| P12 position | ||||
| JP1 position | MULTI configuration position | |||
| CN0418 Setup (if available) | ||||
| P10 position | Any position from MULTI configuration |
| P9 position | ||||
| JP2 position | Any position to result a different EEPROM address from board to board |
| JP3 position | ||||
| JP4 position | ||||
| P17 position | Jumper should be placed to power the whole system | |||
| EVAL-ADICUP3029 | ||||
| S2 position | ARDUINO position | |||
| S5 position | WALL/USB position | |||
The CLI program does not need the EVAL-CN0416-ARDZ board and is not affected by it's presence either. Furthermore, the PLC/ single-node DCS configuration can also operate with a direct connection, useful for testing out individual nodes quickly.
| EVAL-ADICUP3029 | |
| S2 position | USB position |
There are four types of standard registers in the MODBUS slave:
| Coil/Register Number | Data addresses | Types | Names |
| 1 - 9999 | 0 to 270E | Read-Write | Discreet Output Coils |
| 10001 - 19999 | 0 to 270E | Read-Only | Discreet Input Contacts |
| 30001 - 39999 | 0 to 270E | Read-Only | Analog Input Registers |
| 40001 - 49999 | 0 to 270E | Read-Write | Output Holding Registers |
Each of these registers have a 16-bit address and a 16-bit value.
The Discreet Output Coils are registers that control a single output wire that has a binary value (high or low). Reading this register returns the output value of the bit and writing to it will update the coil with either low value, for writing 0, or high value, for writing anything else. The Discreet Input Contacts are registers that represent the value of a single input logic wire. The register can be only read and it is 0 if the wire is logic low and 0XFFFF if the wire is logic high. The DCS reference design does not have any functions that would map to Discreet Output Coils or Discreet Input Contacts. The Analog Input Registers represent an analog value, usually from an analog wire. This register can be only read and returns a 16-bit value. The Output Holding Registers are registers that control an analog output or a state of the slave. Reading this register returns the state of a process or an output and writing to it may change them or start a process.
Each register can be accessed using a function code:
| Function code | Action | Table name |
| 1 (0x01) | Read | Discreet Output Coils |
| 5 (0x05) | Write Single | Discreet Output Coils |
| 15 (0x0F) | Write Multiple | Discreet Output Coils |
| 2 (0x02) | Read | Discreet Input Contacts |
| 4 (0x04) | Read | Analog Input Registers |
| 3 (0x03) | Read | Output Holding Registers |
| 6 (0x06) | Write Single | Output Holding Registers |
| 16 (0x10) | Write Multiple | Output Holding Registers |
Because the DCS reference design may contain any combination of up to four input or output boards, as a MODBUS slave, it contains two type of MODBUS registers: common and board specific.
The common registers are 5 read-only registers and 2 read-write registers. In standard MODBUS terminology that translates to 5 analog input registers and 2 holding registers:
| Name | Address | Type | Description |
| Detected boards | 0x0000 | Analog Input Register | Number of input and/or output boards present in the system. |
| First board data | 0x0001 | Analog Input Register | First board type (bit 0), First board CS address (bits 1,2) |
| Second board data | 0x0002 | Analog Input Register | Second board type (bit 0), Second board CS address (bits 1,2) |
| Third board data | 0x0003 | Analog Input Register | Third board type (bit 0), Third board CS address (bits 1,2) |
| Fourth board data | 0x0004 | Analog Input Register | Fourth board type (bit 0), Fourth board CS address (bits 1,2) |
| Update rate MSW | 0x00FE | Output Holding Register | Most significant word of the update rate. |
| Update rate LSW | 0x00FF | Output Holding Register | Least significant word of the update rate. |
The board type bit is “0” for CN0414 and “1” for CN0418.
The update rate is stored as:
Update rate MSW = ((Actual update rate * 10000) & 0xFFFF0000) >> 16; Update rate LSW = ((Actual update rate * 10000) & 0x0000FFFF) >> 0;
So the equation used to retrieve the update rate is:
Or in code form:
Actual update rate = (((Update rate MSW << 16) & 0xFFFF0000) | Update rate LSW) / 10000;
The register map is configured dynamically after power-up. Adding a board to the system adds a number of board specific registers: 50 analog input registers and 7 output holding registers for each EVAL-CN0414-ARDZ, and 30 analog input registers and 10 output holding registers for each EVAL-CN0418-ARDZ.
As stated before, adding an EVAL-CN0414-ARDZ adds 57 registers to the device: 50 analog input registers and 7 output holding registers. The analog input registers are: 16 for ADC input values, 4 for ADC input open wire detection flags and 50 for HART receive buffer. The output holding registers are: 1 for ADC output coding, 1 for ADC filter options, 1 for ADC postfilter options, 1 for ADC output data rate options, 1 for ADC open wire detection enable, 1 for HART command zero and 1 for HART channel select. The output holding registers are: 16 for the channel registers, 4 for Open Wire Detection and 30 for the HART input buffer. Adding an EVAL-CN0418-ARDZ adds 40 registers: 30 analog input registers and 10 output holding registers. There are 30 HART input registers as analog input registers. The output holding registers are: 4 for channel ranges (one for each channel), 4 for the channels output (one for each channel), 1 for the HART active channel and 1 for the HART command zero.
Note that being a dynamic system the registers presented below do not have an unique address, but have an address offset that can be used to calculate their address. The function is:
Address = (ADC_CS_address << 12) + (MODBUS_slave_address << 8) + Address_offset;
Register map for the EVAL-CN0414-ARDZ:
| Name | Address Offset | Type | Description |
| Channel 1 MSW | 0x05 | Analog Input Register | Most significant word of the first ADC channel. |
| Channel 1 LSW | 0x06 | Analog Input Register | Least significant word of the first ADC channel. |
| Channel 2 MSW | 0x07 | Analog Input Register | Most significant word of the second ADC channel. |
| Channel 2 LSW | 0x08 | Analog Input Register | Least significant word of the second ADC channel. |
| Channel 8 MSW | 0x13 | Analog Input Register | Most significant word of the eighth ADC channel. |
| Channel 8 LSW | 0x14 | Analog Input Register | Least significant word of the eighth ADC channel. |
| Channel 1 OWD | 0x15 | Analog Input Register | Open wire detection flag of the first voltage channel. |
| Channel 2 OWD | 0x16 | Analog Input Register | Open wire detection flag of the second voltage channel. |
| Channel 3 OWD | 0x17 | Analog Input Register | Open wire detection flag of the third voltage channel. |
| Channel 4 OWD | 0x18 | Analog Input Register | Open wire detection flag of the fourth voltage channel. |
| HART IN 1 | 0x19 | Analog Input Register | First word of the HART input buffer. |
| HART IN 2 | 0x1A | Analog Input Register | Second word of the HART input buffer. |
| HART IN 30 | 0x36 | Analog Input Register | 50th word of the HART input buffer. |
| ADC Output Code | 0x00 | Output Holding Register | Set the output coding for the ADC: 0 - bipolar coding (default); 1 - unipolar coding. |
| ADC Filter | 0x01 | Output Holding Register | Set the input filter for the ADC: 0 - s5+s1 (default); 1 - s3. |
| ADC Postfilter | 0x02 | Output Holding Register | Set the input postfilter for the ADC: 0 - 27 SPS, 47 dB rejection, 36.7 ms settling; 1 - 25 SPS, 62 dB rejection, 40 ms settling; 2 - 20 SPS, 86 dB rejection, 50 ms settling; 3 - 16.67 SPS, 92 dB rejection, 60 ms settling; 4 - disable postfilter (default). |
| ADC ODR | 0x03 | Output Holding Register | Set the output data rate for the ADC: [0-5] - 31250 SPS (default); 6 - 15625 SPS; 7 - 10417 SPS; 8 - 5208 SPS; 9 - 2597 SPS; 10 - 1007 SPS; 11 - 503.8 SPS; 12 - 381 SPS; 13 - 200.3 SPS; 14 - 100.5 SPS; 15 - 59.52 SPS; 16 - 49.68 SPS; 17 - 20.01 SPS; 18 - 16.63 SPS; 19 - 10 SPS; 20 - 5 SPS; 21 - 2.5 SPS; 22 - 1.25 SPS; |
| ADC OWD EN | 0x04 | Output Holding Register | Enable/disable open wire detection for the ADC: 0 - disable OWD (default); 1 - enable OWD. |
| HART cmd 0 | 0x05 | Output Holding Register | Writing “1” to this register sends HART command 0 then the register resets to “0”. |
| HART CH select | 0x06 | Output Holding Register | Select enable a current channel for HART communication: 0 - Channel 1 (default); 1 - Channel 2; 2 - Channel 3; 3 - Channel 4. |
Register map for the EVAL-CN0418-ARDZ:
| HART IN 1 | 0x05 | Analog Input Register | First word of the HART input buffer. |
| HART IN 2 | 0x06 | Analog Input Register | Second word of the HART input buffer. |
| HART IN 30 | 0x22 | Analog Input Register | 50th word of the HART input buffer. |
| Channel 1 range | 0x00 | Output Holding Register | Output range for the first DAC channel: 0 - 0V to 5V; 1 - 0V to 10V; 2 - -5V to 5V; 3 - -10V to 10V; 4 - 4ma to 20ma; 5 - 0ma to 20ma; 6 - 0ma to 24ma. |
| Channel 2 range | 0x01 | Output Holding Register | Output range for the second DAC channel: 0 - 0V to 5V; 1 - 0V to 10V; 2 - -5V to 5V; 3 - -10V to 10V; 4 - 4ma to 20ma; 5 - 0ma to 20ma; 6 - 0ma to 24ma. |
| Channel 3 range | 0x02 | Output Holding Register | Output range for the third DAC channel: 0 - 0V to 5V; 1 - 0V to 10V; 2 - -5V to 5V; 3 - -10V to 10V; 4 - 4ma to 20ma; 5 - 0ma to 20ma; 6 - 0ma to 24ma. |
| Channel 4 range | 0x03 | Output Holding Register | Output range for the fourth DAC channel: 0 - 0V to 5V; 1 - 0V to 10V; 2 - -5V to 5V; 3 - -10V to 10V; 4 - 4ma to 20ma; 5 - 0ma to 20ma; 6 - 0ma to 24ma. |
| Channel 1 | 0x04 | Output Holding Register | Output code of the first DAC channel. |
| Channel 2 | 0x05 | Output Holding Register | Output code of the second DAC channel. |
| Channel 3 | 0x06 | Output Holding Register | Output code of the third DAC channel. |
| Channel 4 | 0x07 | Output Holding Register | Output code of the fourth DAC channel. |
| HART cmd 0 | 0x08 | Output Holding Register | Writing “1” to this register sends HART command 0 then the register resets to “0”. |
| HART CH select | 0x09 | Output Holding Register | Select enable a current channel for HART communication: 0 - Channel A (default); 1 - Channel B; 2 - Channel C; 3 - Channel D. |
The software can be set up to work in CLI debug mode or in MODBUS mode. To set this make sure the relevant define in the config.h file is uncommented and the other one is commented:
//#define CLI_INTEFACE //#define MODBUS_INTERFACE
There are two interfaces available for this application: a Command Line Interface (CLI) used mainly for debugging a single PLC node and a MODBUS interface used for PLC/DCS operation for single and multiple nodes.
The CLI is implemented through UART and must be connected to a computer via USB cable. A serial terminal program must run on the host PC to display data and control the application.
The MODBUS is connected through the EVAL-CN0416-ARDZ UART to RS485 adapter and must communicate with a MODBUS master on the RS485 line.
A serial terminal is an application that runs on a PC or laptop that is used to display data and interact with a connected device (including many of the Circuits from the Lab reference designs). The device's UART peripheral is most often connected to a UART to USB interface IC, which appears as a traditional COM port on the host PC/ laptop. (Traditionally, the device's UART port would have been connected to an RS-232 line driver / receiver and connected to the PC via a 9-pin or 25-pin serial port.) There are many open-source applications, and while there are many choices, typically we use one of the following:
Before continuing, please make sure you download and install one of the above programs.
There are several parameters on all serial terminal programs that must be setup properly in order for the PC and the connected device to communicate. Below are the common settings that must match on both the PC side and the connected UART device.
In many instances there are other options that each of the different serial terminal applications provide, such as local line echo or local line editing, and features like this can be turned on or off depending on your preferences. This setup guide will not go over all the options of each tool, but just the minor features that will make it easier to read back data from the connected devices.
Example setup using Putty
Typing help or h after initial calibration sequence will display the list of commands and their short versions. The CLI mode has a board command menu which is only used to select the board. Each board present in the system has it's own command set based on the type.
Bellow is the short command list for the board menu:
| Command | Description |
| h | Display available commands. |
| bs | Set the active board. <board_no> = de ID of the board assigned by the program. It its displayed at the start of the program. Calling this command without an argument displays available boards again. |
The specific commands for each of the types of boards is described in they respective wiki pages:
The Modbus protocol is not human-readable; as such, a Modbus master program is required to interact with the design. QModMaster is a free and open-source implementation of a Modbus master GUI application. This program is useful for board bringup and debug, and during application development. QModMaster is avalable at QModMaster on SourceForge
QModMaster is used to demonstrate several basic register operations below.
We recommend not opening the project directly, but rather import it into CrossCore Embedded Studios and make a local copy in your workspace.
The source code and include files of the ADuCM3029_demo_cn0435 can be found here:
The official tool we promote for use with the EVAL-ADICUP3029 is CrossCore Embedded Studio. For more information on downloading the tools and a quick start guide on how to use the tool basics, please check out the Tools Overview page.
For more detailed instructions on importing this application/demo example into the CrossCore Embedded Studios tools, please view our How to import existing projects into your workspace section.
For more detailed instructions on importing this application/demo example into the CrossCore Embedded Studios tools, please view our How to configure the debug session section.
The application controls a dynamic system that can be physically different every time it is run. to do this it has two parts:
After getting parameters of the system supplied by the user in code the program initializes the software modules common to all the boards: I2C, UART, SPI, microcontroller power, software UART and the AD5700 HART modem. If the MODBUS interface is used, the update timer for the input boards is also initialized in this stage as a common module. If, by comparison, the CLI is used, each input board present initializes its own version of the update timer driver.
After these initializations the system runs a board discovery routine. By using the presence of I2C EEPROM memory and testing the SPI configuration, all boards in the system are discovered and labeled as either CN0414 or CN0418. If the MODBUS interface is used, the system also scans for its MODBUS slave address and maps and initializes MODBUS registers.
After board discovery, if the CLI is used, no board is set as active and the system manager loads the main menu process. If the MODBUS is used, the system activates the first board it discovers.
If the CLI is used, no board is active after the initialization and the system stands by to receive commands. If the user sets one of the boards to be active, the program loads the commands and process specific to that board and starts sunning them until the application is stopped or the “exit” command is called.
If the MODBUS interface is used the first board discovered is the active board. If it is a CN0414 the program runs its process until all channels are updated. If it is a CN0418 the program runs its process only once. After this the system deactivates the board and activates the next board discovered until all the boards have been active and updated. The system than cycles back from the beginning.
Meanwhile the system scans the MODBUS channel for commands and if one is found that is addressed to this node it executes it and sends back a response.
The process and commands for each type of boards is described in the appropriate application page:
User DCS programs running on the host will be highly application-specific, and written in any number of languages. This section presents several example applications and utilities written in Python that perform basic functions such as reading and writing analog voltages, detecting the configuration of a node, and changing the data rate of an analog input channel.
The following utility functions are demonstrated using the single-node configuration described above. It may be connected to the host either directly via USB (no RS485 interface) or over a USB to RS485 bridge. Minimalmodbus is an open-source (Apache license) Modbus RTU and Modbus ASCII implementation for Python, and is used in these examples. Similar libraries exist for other languages.
For example, consider an instrument (slave) with Modbus RTU and address number 1 to which we are to communicate via a serial port with the name COM12. The instrument stores the actual configuration in registers 0 to 4. To read data from the instrument:
"""Read common analog input registers to determine PLC/DCS configuration.""" import minimalmodbus # declare an instrument object with port name, slave address as input arguments INSTRUMENT = minimalmodbus.Instrument('COM12', 1) # read 5 registers starting from address 0 by using function code 4 COMMON_ANALOG_INPUT_REGISTERS = INSTRUMENT.read_registers( registeraddress=0, numberOfRegisters=5, functioncode=4) # result a list with 5 elements in decimal format print(COMMON_ANALOG_INPUT_REGISTERS)
[4, 1, 3, 4, 6]
In this example, after we run the above piece of code it results that we have 4 boards connected. Two of this boards are EVAL-CN0414-ARDZ and other two are EVAL-CN0418-ARDZ. The EVAL-CN0414-ARDZ boards have address 0b10 and 0b11 while EVAL-CN0418-ARDZ boards have address 0b00 and 0b01.
Next, if we want to read all analog input channels from one EVAL-CN0414-ARDZ we can use the following:
"""Read analog input registers to determine ADC channels code.""" import minimalmodbus # declare an instrument object with port name, slave address as input arguments INSTRUMENT = minimalmodbus.Instrument('COM12', 1) # read 16 registers starting from address 12549 by using function code 4 ADC_CHANNELS_CODES = INSTRUMENT.read_registers( registeraddress=12549, numberOfRegisters=16, functioncode=4) # result a list with 16 elements in decimal format print(ADC_CHANNELS_CODES)
[127, 65158, 127, 65514, 127, 65194, 127, 64995, 127, 65285, 127, 65244, 127, 65292, 127, 65278]
In this example, after we run the above piece of code it results a list of 16 elements in decimal format. First 8 values corespond to voltage channels and last to current channels.
Next, if we want to change the output code of one EVAL-CN0414-ARDZ ADC to be unipolar instead of bipolar we can use the following:
"""Read and write one output holding register to change ADC output code.""" import minimalmodbus # declare an instrument object with port name, slave address as input arguments INSTRUMENT = minimalmodbus.Instrument('COM12', 1) # read a single register from address 12544 by using function code 3 INITIAL_ADC_OUTPUT_CODE = INSTRUMENT.read_register( registeraddress=12544, functioncode=3) # result an integer print(INITIAL_ADC_OUTPUT_CODE) # wrie a single register from address 12544 by using function code 6 INSTRUMENT.write_register(registeraddress=12544, value=1, functioncode=6) # read a single register from address 12544 by using function code 3 FINAL_ADC_OUTPUT_CODE = INSTRUMENT.read_register( registeraddress=12544, functioncode=3) # result an integer print(FINAL_ADC_OUTPUT_CODE)
0 1
In this example, after we run the above piece of code it results an integer which coresponds to ADC coding format. The default value 0, indicate that the ADC is set to bipolar coding format, while a value of 1 will indicate an unipolar coding format.
Next, if we want to change the output code of one EVAL-CN0418-ARDZ DAC channel we can use the following:
"""Read and write one output holding register to change DAC channel voltage.""" import minimalmodbus # declare an instrument object with port name, slave address as input arguments INSTRUMENT = minimalmodbus.Instrument('COM12', 1) # read a single register from address 4356 by using function code 3 INITIAL_DAC_CHANNEL_1_CODE = INSTRUMENT.read_register( registeraddress=4356, functioncode=3) # result an integer print(INITIAL_DAC_CHANNEL_1_CODE) # wrie a single register from address 4356 by using function code 6 INSTRUMENT.write_register(registeraddress=4356, value=65535, functioncode=6) # read a single register from address 4356 by using function code 3 FINAL_DAC_CHANNEL_1_CODE = INSTRUMENT.read_register( registeraddress=4356, functioncode=3) # result an integer print(FINAL_DAC_CHANNEL_1_CODE)
0 65535
In this example, after we run the above piece of code it results an integer which coresponds to DAC channel 1 output code. Depending on channel configuration this output code will corespond to a voltage or a current value. In this example the DAC channel output code is by default 0V because the default channel range is set to 0V to 5V. The 65535 value will corespond in this case to a 5V output.
Next, if we want to determine the system configuration we can run the following script from the attached archive.
For a PLC configuration the script output will look similarly like this:
Welcome! Use 'CTRL+C' to go back from the current menu or exit! Available devices: 1 -> Silicon Labs CP210x USB to UART Bridge (COM12) 2 -> Intel(R) Active Management Technology - SOL (COM3) Enter detected device index, or press ENTER to use COM12: No boards at MODBUS address: 1 No communication with the instrument (no answer) Boards found at MODBUS address: 2 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 4 0002 (0x0002) Second board data 6 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 Analog input board at address: 10 Analog input board at address: 11 No boards at MODBUS address: 3 No communication with the instrument (no answer) No boards at MODBUS address: 4 No communication with the instrument (no answer) No boards at MODBUS address: 5 No communication with the instrument (no answer) No boards at MODBUS address: 6 No communication with the instrument (no answer) No boards at MODBUS address: 7 No communication with the instrument (no answer) No boards at MODBUS address: 8 No communication with the instrument (no answer) No boards at MODBUS address: 9 No communication with the instrument (no answer) No boards at MODBUS address: 10 No communication with the instrument (no answer) No boards at MODBUS address: 11 No communication with the instrument (no answer) No boards at MODBUS address: 12 No communication with the instrument (no answer) No boards at MODBUS address: 13 No communication with the instrument (no answer) No boards at MODBUS address: 14 No communication with the instrument (no answer) No boards at MODBUS address: 15 No communication with the instrument (no answer) No boards at MODBUS address: 16 No communication with the instrument (no answer)
For a DCS configuration the script output will look similarly like this:
Welcome! Use 'CTRL+C' to go back from the current menu or exit! Available devices: 1 -> Silicon Labs CP210x USB to UART Bridge (COM12) 2 -> Intel(R) Active Management Technology - SOL (COM3) Enter detected device index, or press ENTER to use COM12: Boards found at MODBUS address: 1 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 1 0002 (0x0002) Second board data 3 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 Analog output board at address: 00 Analog output board at address: 01 Boards found at MODBUS address: 2 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 4 0002 (0x0002) Second board data 6 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 Analog input board at address: 10 Analog input board at address: 11 No boards at MODBUS address: 3 No communication with the instrument (no answer) No boards at MODBUS address: 4 No communication with the instrument (no answer) No boards at MODBUS address: 5 No communication with the instrument (no answer) No boards at MODBUS address: 6 No communication with the instrument (no answer) No boards at MODBUS address: 7 No communication with the instrument (no answer) No boards at MODBUS address: 8 No communication with the instrument (no answer) No boards at MODBUS address: 9 No communication with the instrument (no answer) No boards at MODBUS address: 10 No communication with the instrument (no answer) No boards at MODBUS address: 11 No communication with the instrument (no answer) No boards at MODBUS address: 12 No communication with the instrument (no answer) No boards at MODBUS address: 13 No communication with the instrument (no answer) No boards at MODBUS address: 14 No communication with the instrument (no answer) No boards at MODBUS address: 15 No communication with the instrument (no answer) No boards at MODBUS address: 16 No communication with the instrument (no answer)
Next, if we want to check or change the system registers we can run the following script from the attached archive.
Depending on the system configuration, one or more DCS nodes will be detected. After the user selects a valid DCS node, a menu will appear which contain all available system options. Now, depending on the node configuration, not all option will be valid, even if they are shown. For example, if a DCS node doesn't contain CN0414 analog input board(s), any option which refers to CN0414 will do nothing.
Welcome! Use 'CTRL+C' to go back from the current menu or exit! Available devices: 1 -> Silicon Labs CP210x USB to UART Bridge (COM12) 2 -> Intel(R) Active Management Technology - SOL (COM3) Enter detected device index, or press ENTER to use COM12: Enter MODBUS timeout (0.05[s] to inf), or press ENTER to use 0.1[s] timeout: Boards found at MODBUS address: 1 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 1 0002 (0x0002) Second board data 3 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 analog output board at address: 00 analog output board at address: 01 Boards found at MODBUS address: 2 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 4 0002 (0x0002) Second board data 6 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 analog input board at address: 10 analog input board at address: 11 No boards at MODBUS address: 3 No communication with the instrument (no answer) No boards at MODBUS address: 4 No communication with the instrument (no answer) No boards at MODBUS address: 5 No communication with the instrument (no answer) No boards at MODBUS address: 6 No communication with the instrument (no answer) No boards at MODBUS address: 7 No communication with the instrument (no answer) No boards at MODBUS address: 8 No communication with the instrument (no answer) No boards at MODBUS address: 9 No communication with the instrument (no answer) No boards at MODBUS address: 10 No communication with the instrument (no answer) No boards at MODBUS address: 11 No communication with the instrument (no answer) No boards at MODBUS address: 12 No communication with the instrument (no answer) No boards at MODBUS address: 13 No communication with the instrument (no answer) No boards at MODBUS address: 14 No communication with the instrument (no answer) No boards at MODBUS address: 15 No communication with the instrument (no answer) No boards at MODBUS address: 16 No communication with the instrument (no answer) Enter MODBUS address from this list [1, 2], or press ENTER to use MODBUS address 1: Enter commands delay (0[s] to inf), or press ENTER to use 0.1[s] delay: Test options: 1 - Read common analog input registers. 2 - Read common output holding registers. 3 - Read analog input registers. 4 - Read output holding registers. 5 - Write output holding register. q - Quit. Enter test option:
The following section presents several example top-level DCS applications. Like the utilities, these are based on Minimalmodbus.
This application provides a simple way to control a DCS system and also to detect HART devices by using the HART protocol.
The HART protocol is proprietary, customers implementing a full HART stack should refer to https://fieldcommgroup.org This reference design provides a basic implementation of “command zero” that can be used to verify connectivity with HART instruments. CN0267 is a Complete 4 mA to 20 mA Loop Powered Field Instrument with HART Interface that can be used to test the DCS HART functionality. This application allows to:
Welcome! Use 'CTRL+C' to go back from the current menu or exit! Available devices: 1 -> Silicon Labs CP210x USB to UART Bridge (COM12) 2 -> Intel(R) Active Management Technology - SOL (COM3) Enter detected device index, or press ENTER to use COM12: Enter MODBUS timeout (0.05[s] to inf), or press ENTER to use 0.1[s] timeout: Boards found at MODBUS address: 1 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 1 0002 (0x0002) Second board data 3 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 analog output board at address: 00 analog output board at address: 01 Boards found at MODBUS address: 2 Address Name Value ------------- ----------------- ------- 0000 (0x0000) Detected boards 2 0001 (0x0001) First board data 4 0002 (0x0002) Second board data 6 0003 (0x0003) Third board data 65535 0004 (0x0004) Fourth board data 65535 analog input board at address: 10 analog input board at address: 11 No boards at MODBUS address: 3 No communication with the instrument (no answer) No boards at MODBUS address: 4 No communication with the instrument (no answer) No boards at MODBUS address: 5 No communication with the instrument (no answer) No boards at MODBUS address: 6 No communication with the instrument (no answer) No boards at MODBUS address: 7 No communication with the instrument (no answer) No boards at MODBUS address: 8 No communication with the instrument (no answer) No boards at MODBUS address: 9 No communication with the instrument (no answer) No boards at MODBUS address: 10 No communication with the instrument (no answer) No boards at MODBUS address: 11 No communication with the instrument (no answer) No boards at MODBUS address: 12 No communication with the instrument (no answer) No boards at MODBUS address: 13 No communication with the instrument (no answer) No boards at MODBUS address: 14 No communication with the instrument (no answer) No boards at MODBUS address: 15 No communication with the instrument (no answer) No boards at MODBUS address: 16 No communication with the instrument (no answer) Enter MODBUS address from this list [1, 2], or press ENTER to use MODBUS address 1: Enter commands delay (0[s] to inf), or press ENTER to use 0.1[s] delay: Use CTRL+C to end a process or switch between nodes. CN0414 CN0418 CN0435 ------------------------------------- ---------------------------- ---------------------------------------- 1 - Read device voltage channel e - Set DAC channel 1 output o - Read common analog input registers 2 - Read device current channel f - Set DAC channel 2 output p - Read common output holding registers 3 - Read board voltage channels g - Set DAC channel 3 output r - Read analog input registers 4 - Read board current channels h - Set DAC channel 4 output s - Read output holding registers 5 - Read instrument voltage channels i - Set DAC channel 1 range t - Detect system configuration 6 - Read instrument current channels j - Set DAC channel 2 range 7 - Set ADC output code k - Set DAC channel 3 range 8 - Set ADC filter l - Set DAC channel 4 range 9 - Set ADC postfilter m - Send HART command zero a - Set ADC output data rate n - Select HART channel b - Set ADC open wire detection state c - Send HART command zero d - Select HART channel q - Quit Enter Option:
End of Document